Good mornin,

I plan on taking over half our garage (maybe more) for my new woodshop. I think I have plenty of space, but power is a problem. There is only one 15 amp circuit from the house and the lights dim when the Miter Saw winds up.

I know I'm gonna have to have more circuits run, but not sure if I need additional service from The Electric Company. My 120 year old house only has 100 amps, but I do have 2 or 3 spare breakers (1 15 amp circuit just running to the outlet in the crawl space).

Advice? I've just bought a router, jointer and planer so I'd like to spend as little as possible on this...LOL.

Thanks,
Chris
NortonChris is offline   Top - Reply with Quote
Alt Sponsor Post
Advertising



Alt Sponsored Links

__________________
This advertising will not be shown in this way to registered members.
Register your free account today and become a member on Router Forums
   
Old 11-04-2007, 10:57 AM   #2
challagan
Retired Moderator
Supreme Forum King
 
challagan's Avatar
 
Join Date: Feb 2006
Location: Iowa
Posts: 4,002
challagan is on a distinguished road


15 Amps won't cut it for many bigger tools. I had to redo my panel and add 20 amp circuits. My table saw while rated for 15 amps actually used more to get it started... in other words the draw was higher on start up.... it would blow the fuse. So I ended up putting 3 - 20 amp circuits in the shop. If it dims now with the miter saw, most likely it will blow with a table saw or a planer.

Corey
__________________
My Carving Website: The Iowa Woodcarver
http://iowacarver.tripod.com/

My Shop Website - Woodshop 51503
http://woodshop51503.tripod.com/
challagan is offline   Top - Reply with Quote
Old 11-04-2007, 11:17 AM   #3
bobj3
Forum Contributer
Supreme Forum King
 
bobj3's Avatar
 
Join Date: Jan 2006
Location: Littleton,Colorado U.S.A.
Posts: 8,299
bobj3 is a jewel in the roughbobj3 is a jewel in the roughbobj3 is a jewel in the rough


Hi Chris

The 1st thing you want to do is check the load panel and see if the other spare breakers are marked 20amp. if so find the breaker that is being used for the garage and pull the wire out of that breaker and put it in one of the other ones marked 20 amp.

If you don't have one you can pull one of the breakers and take it to HomeDepot/Lowes and get a 20 amp. breaker, one you can pop in..that should help for just a little bit..

A good rule to go by is to walk around the shop and write down all the tools you have and write down the amps they pull that will give you a idea what kind of service you will need in the shop..then div. that by 2 ,because you will never have all them running at one time...but this just a swag rule of thumb but do think down the road,,,a 220 volt drop to shop is nice, that will give you two 110 volt drops.in one so to speak..or if you get a bigger power tool you will have the power for it without a rework ...update...

You didn't say if the garage/shop is next to the house if so it will be easy to get more power/out lets to the shop BUT if not will need to update/drop to the service to the garage..

Some of the old homes have just two wires running to the garage and you need to update that..

It's always best to over update ,that's to say a new load center panel (breaker box) to a 200 amp. service...but this will take a new elec.permit you can pull the permit as a home owner but you may want to call a lic. electrician to check it out and give you and hand...

I should note you can do it all it's not hard it just takes a bit of home work.

BUT the bottom line,, it just maybe wire size ,you said the lights would dim, that's a real tip off the norm..that the wire size is to small..

Think of like a water line,, 1/2" line it can only let so much water run but if you use 3/4" water line ,all the water outlets have what they need...

So it maybe time to use the other Spare breakers you have and run some more wire to the shop...two 20 amp. lines should do the job for now.

==============







Quote:
Originally Posted by NortonChris
Good mornin,

I plan on taking over half our garage (maybe more) for my new woodshop. I think I have plenty of space, but power is a problem. There is only one 15 amp circuit from the house and the lights dim when the Miter Saw winds up.

I know I'm gonna have to have more circuits run, but not sure if I need additional service from The Electric Company. My 120 year old house only has 100 amps, but I do have 2 or 3 spare breakers (1 15 amp circuit just running to the outlet in the crawl space).

Advice? I've just bought a router, jointer and planer so I'd like to spend as little as possible on this...LOL.

Thanks,
Chris
__________________
PodCast videos
RWS on YouTube

http://www.routerforums.com/86898-post1.html
Besure and click on the Up Arrow key ▲ on the Youtube video, you can select other youtube videos on router tables
http://www.woodworkingonline.com/?s=dovetail
Machine Cut ▼
http://www.woodworkingonline.com/200...cut-dovetails/

http://www.woodworkingonline.com/woo...podcast-store/

http://www.woodshopdemos.com/menu2.htm

Bob J.


Last edited by bobj3; 11-05-2007 at 09:28 AM.
bobj3 is offline   Top - Reply with Quote
Old 11-04-2007, 11:19 AM   #4
Joe Lyddon
Banned
Supreme Forum King
 
Joe Lyddon's Avatar
 
Join Date: Sep 2004
Location: Alta Loma, CA USA
Posts: 2,168
Joe Lyddon is on a distinguished road


Quote:
Originally Posted by challagan
15 Amps won't cut it for many bigger tools. I had to redo my panel and add 20 amp circuits. My table saw while rated for 15 amps actually used more to get it started... in other words the draw was higher on start up.... it would blow the fuse. So I ended up putting 3 - 20 amp circuits in the shop. If it dims now with the miter saw, most likely it will blow with a table saw or a planer.

Corey

Ditto...

And remember...
NORMALLY, there will be only ONE tool turned on at one time... except for dust collection (someday, if not today). Two good circuits to handle that... plus another one to make it more convenient.

That's exactly what I'm planning on doing, in addition to a 220 circuit, of course.
Joe Lyddon is offline   Top - Reply with Quote
Old 11-04-2007, 11:42 AM   #5
Noddy
Registered User
Forum Fanatic
 
Noddy's Avatar
 
Join Date: Aug 2007
Location: N. Ca
Posts: 105
Noddy is on a distinguished road


The other thing you might consider doing is running a new leg to the garage and installing a new / separate sub-panel. From that, you can pick your amperage. A 75 amp sub panel should fit right in, provide all the power you need, and bring your shop up to date and get away from the 100 year / older 100 amp panel which is (as it sounds) pretty maxed out as far as expansion is concerned.
__________________
Regards-
Noddy
Noddy is offline   Top - Reply with Quote
Old 11-04-2007, 12:05 PM   #6
Joe Lyddon
Banned
Supreme Forum King
 
Joe Lyddon's Avatar
 
Join Date: Sep 2004
Location: Alta Loma, CA USA
Posts: 2,168
Joe Lyddon is on a distinguished road


Quote:
Originally Posted by Noddy
The other thing you might consider doing is running a new leg to the garage and installing a new / separate sub-panel. From that, you can pick your amperage. A 75 amp sub panel should fit right in, provide all the power you need, and bring your shop up to date and get away from the 100 year / older 100 amp panel which is (as it sounds) pretty maxed out as far as expansion is concerned.
Yes... I forgot to mention that...
Joe Lyddon is offline   Top - Reply with Quote
Old 11-04-2007, 12:21 PM   #7
Woodnut65
Registered User
Forum Geek
 
Join Date: Oct 2004
Posts: 345
Woodnut65 is on a distinguished road


Hi: The 100 Amp service that is to the house will not likely be enough, and should be updated to 200Amp service at220 volts. Changing breakers from 15 Amp to twenty amp is not agood idea since 15 Amp circuits are used for lighting and are usually run
using Number 14 cable which is not for 20 Amp service. For that you need size 12 wiring. On start up any motor will draw from two to four times the run current listed on the motor info. If the circuit is adequate the breaker may not trip since most breakers are made to carry a temporary start up current load. But you don't say what is being powered in the house. Like Air Condtioning, Washer, and dryer circuits etc.
I suggest you get an electrician to check the whole thing over and make a recomendation and cost estimate for you to consider. Hope this helps, Woodnut65
Woodnut65 is offline   Top - Reply with Quote
Old 11-04-2007, 12:47 PM   #8
Hamlin
Registered User
Supreme Forum King
 
Hamlin's Avatar
 
Join Date: Dec 2005
Location: Baldwin City, KS
First Name: Ken
Posts: 1,575
Hamlin is an unknown quantity at this point

Send a message via MSN to Hamlin

Best choice would be replace existing panel, switching to a 200amp as Woodnut suggested. I suggest a newer panel for this reason, you will have the space for adding additional circuits if and when needed. Your breakers should be 20amps.

Whichever way you decide to go from other suggestions, you will still need to update to a 200amp service panel. Changing these out aren't that difficult.
__________________
Ken

"A VETERAN"
"Whether active duty, retired, national guard or reserve - is someone who, at one point in their life, wrote a blank check made payable to "The United States of America", for an amount of "up to and including my life". That is HONOR, and there are way too many people in this country who no longer understand it." -Author Unknown
Hamlin is offline   Top - Reply with Quote
Old 11-04-2007, 03:09 PM   #9
kp91
Marine Engineer
Forum King
 
kp91's Avatar
 
Join Date: Sep 2004
Location: Fredericksburg, VA
First Name: Doug
Posts: 921
kp91 is on a distinguished road


Woodnut-

You beat me to the point. Just changing a breaker doesn't turn a 15 amp circuit into a 20 amp. The conductor size is the important factor. You may have big enough cable, but better check first. A lot of new houses aren't putting any more copper than they have to, so be leary about swapping out breakers there as well.

I would recommend getting an electrician out to survey your situation, mainly for insurance purposes should something go wrong later. If you cobble something together and the worse should happen, you may not be fully covered.

That being said, if you are going to put some money in your shop electrical system, do it right from the get go. Leave the existing circuit for lighting, garage door opener, battery charger outlet, etc., and add a sub panel with a disconnect switch. Off of that panel, run an additional lighting circuit, a couple of 20 amp power tool receptacle circuits, and 2 220v receptacle circuits. This way, as your shop 'matures', you can have the big air compressor, dust collector, or the jointer to run on 220.

The disconnect switch is nice, because once you are done in your shop you can kill everything at once. This prevents the air compressor from firing up in the middle of the night should you forget to turn it off.

It will probably set you back a few bucks, but it's worth it. You may find that your local code requires GFCI units in your garage, or that all receptacles have to be positioned a certain height off of the floor. A good electrician will know what you need. You may be able to save a few bucks by running the conduit and mounting the boxes yourself, and have him just do the hook ups.


Just a few thoughts,
__________________
Doug
1 John 1:9
kp91 is offline   Top - Reply with Quote
Old 11-04-2007, 03:14 PM   #10
challagan
Retired Moderator
Supreme Forum King
 
challagan's Avatar
 
Join Date: Feb 2006
Location: Iowa
Posts: 4,002
challagan is on a distinguished road


Quote:
Originally Posted by Woodnut65
Hi: The 100 Amp service that is to the house will not likely be enough, and should be updated to 200Amp service at220 volts. Changing breakers from 15 Amp to twenty amp is not agood idea since 15 Amp circuits are used for lighting and are usually run
using Number 14 cable which is not for 20 Amp service. For that you need size 12 wiring. On start up any motor will draw from two to four times the run current listed on the motor info. If the circuit is adequate the breaker may not trip since most breakers are made to carry a temporary start up current load. But you don't say what is being powered in the house. Like Air Condtioning, Washer, and dryer circuits etc.
I suggest you get an electrician to check the whole thing over and make a recomendation and cost estimate for you to consider. Hope this helps, Woodnut65
That is right, I had to completely change my panel.... upgraded the service to I believe 150 amps and 3 dedicated 20 amp lines for the shop and still have more room for future expansion ( used up 1 for the dishwasher in the remodel) and changed everything from fuses to circuit breakers as well while at it. My brother is an electrician so he helped out greatly here.

Corey
__________________
My Carving Website: The Iowa Woodcarver
http://iowacarver.tripod.com/

My Shop Website - Woodshop 51503
http://woodshop51503.tripod.com/
challagan is offline   Top - Reply with Quote
New Reply

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Ed's Shop karateed Lobby 12 01-21-2008 11:50 PM
Doyle's work shop Doyle Show N' Tell 24 09-06-2007 11:07 PM
A Little Tour of my Little Shop!.... challagan Tools and Woodworking 23 08-26-2007 02:07 PM
shop vacs? CanuckBeaver General Routing 10 06-22-2006 03:15 PM
Just some Shop Snapshots bobj3 Show N' Tell 8 06-16-2006 10:29 PM

RouterWorkshop.net - EagleAmerica.com – Over 2,000 Router Bits - Your Advertisement Here! - Your Advertisement Here! - Your Advertisement Here!

RouterForums.com - Your online woodworking community!
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd. Copyright © 2008 - 2009 RouterForums.com Search Engine Optimization by vBSEO 3.2.0
Professional Web Hosting Solutions provided by: BeastInternet.com