Just picked up a used Delta 50-850 dust control unit. It is wired for 220v and based on what I've read I don't want to run it at 110v. So the question is how to I bring a 200 line to the dust control unit. I've added 110v circuits, but never 220v lines. The motor has a three wire plug on it.
Bob Blooms is offline  
Sponsored Links
Advertisement
 
post #2 of 112 (permalink) Old 07-28-2009, 04:14 PM
Forum Contributor
 
xplorx4's Avatar
 
Join Date: Dec 2008
Country: United States
First Name: Jerry
Posts: 10,671
 
Default

Greetings and welcome to the router forum. Bob if you are not at least some what familiar with the innerworkings of an electrical panel, I think you might find a good eledtrican to run the circut for you. I kGreetings and welcome to the router forum. Bob if you are not at least somewhat familiar with the inner workings of an electrical panel, I think you might find a good electrician to run the circuit for you. I know I can do it but I would be very reluctant to try and explain it in a forum. I hope you can find one soon and get your unit up and running before too long,now I can do it but I would be very reluctant to try and explain it in a forum. I hope you can find one soon and get your unit up and running before to long,

Wisdom: Where experience and knowledge combine and become one.

"We are all one decision away from Stupid!!"

Lamentations 3:22-23

"How often we sacrifice the permanent plans of God on the altar of immediate solutions"

I have a very good memory, just short is all.
xplorx4 is offline  
post #3 of 112 (permalink) Old 07-28-2009, 06:28 PM
Registered User
 
levon's Avatar
 
Join Date: Sep 2008
Country: United States
First Name: levon
Posts: 1,820
 
Default

hi Bob

if you feel comfortable wiring 110 im sure you can wire the 220. some here try to make it rocket science, it isnt. i wired my shop a/c to run on 220. i would advise you to do research on it.im sure you can handle it. but if you think you cant dont attempt it!

light travels faster than sound, this is why some people seem bright til you hear them speak.

Please Please Please edit your profile with a name and location so we can better assist you and make for a friendlier forum

levon
levon is offline  
Sponsored Links
Advertisement
 
post #4 of 112 (permalink) Old 07-28-2009, 06:45 PM
Forum Contributor
 
Join Date: Jan 2006
Country: United States
First Name: Bj
Posts: 23,786
       
Default

Hi Bob

I have 220 ,100 amp service in the shop but run the dust control system on 110 volt,, it only runs a very short time the norm...
Some tools it's must have item to get them to run in the shop,,so to say ,save the 220 when you really need it,,
If you put your money into a remote control box you can turn it on only when you need it and not into 220 line to run the system..

The only thing I use the 220 volt is for the tools that need it like table saw.welders,5 hp compressor, etc..


But that's just my 2 cents ..


======

Quote:
Originally Posted by Bob Blooms View Post
Just picked up a used Delta 50-850 dust control unit. It is wired for 220v and based on what I've read I don't want to run it at 110v. So the question is how to I bring a 200 line to the dust control unit. I've added 110v circuits, but never 220v lines. The motor has a three wire plug on it.



"It's fine to disagree with other members as long as you respect their opinions"

Marc Sommerfeld Tools ,Videos
http://www.youtube.com/channel/UCT-n...RWaEpMA/videos

Find all threads started by bobj3
http://www.routerforums.com/search.php?searchid=944097



Last edited by bobj3; 07-30-2009 at 09:02 PM.
bobj3 is offline  
post #5 of 112 (permalink) Old 07-28-2009, 07:14 PM
Forum Contributor
 
Join Date: Jun 2009
Country: United States
First Name: John
Posts: 3,046
 
Talking

Hi Bob, Welcome to the forums,
Levon is right, 220 isn't exactly rocket science but the other poster was also right in that if you are not comfortable working inside a breaker box. Leave it to an electrician.
220 simply put, is two 110volt lines that are out of phase with each other.
Running the wiring is not different than running a 110 line except it is larger, for a 30 amp device, which I suspect your DC is, you would likely need to run 12-3 w/ground. At the device, wire according to the label instructions, should be one on or near the motor. At the breaker box you need to locate two ADJACENT open circuits, attach the red and black wires to the output sides of the double breaker and attach the white wire to the neutral buss and the ground to the ground bus. In some areas both neutral and ground are attached to the same bus. Then install the breaker.
I tried not to get to detailed so if you understand this you are probably good to go, if you didn't you may want to consider an electrician or a friend to do the final connections after you have run the wiring.
Good Luck,

John Schaben

The problem with experience is I usually get it immediately after I need it.
jschaben is offline  
post #6 of 112 (permalink) Old 07-28-2009, 07:54 PM
Registered User
 
levon's Avatar
 
Join Date: Sep 2008
Country: United States
First Name: levon
Posts: 1,820
 
Default

"attach the red and black wires to the output sides of the double breaker and attach the white wire to the neutral buss and the ground to the ground bus. In some areas both neutral and ground are attached to the same bus. Then install the breaker"

its just that simple, i was thinking of how i wired my a/c and thats exactly how i wired it.
black to hot, red to hot, white to neutral, ground to ground. i wanted to make sure before i told you. anyone that cant explain it to you should not be wiring 220.

but as i said before, if you feel you cant , dont attempt it!

light travels faster than sound, this is why some people seem bright til you hear them speak.

Please Please Please edit your profile with a name and location so we can better assist you and make for a friendlier forum

levon
levon is offline  
post #7 of 112 (permalink) Old 07-28-2009, 08:06 PM
Retired Moderator
 
Hamlin's Avatar
 
Join Date: Dec 2005
Country: United States
First Name: Ken
Posts: 3,437
 
Send a message via MSN to Hamlin
Default

First, you need a proper size breaker for the tool, also make sure to get the correct size of receptacle for the plug. These are rated in amps. Pending on the length of run you'll need, this will determine the correct size of wire as well.

Ken

***Please fill in your profile, at least your location. As this will help us help you better.***

"A VETERAN"
"Whether active duty, retired, national guard or reserve - is someone who, at one point in their life, wrote a blank check made payable to "The United States of America", for an amount of "up to and including my life". That is HONOR, and there are way too many people in this country who no longer understand it." -Author Unknown

Hamlin is offline  
post #8 of 112 (permalink) Old 07-28-2009, 08:20 PM
Forum Contributor
 
xplorx4's Avatar
 
Join Date: Dec 2008
Country: United States
First Name: Jerry
Posts: 10,671
 
Default

Let's take a second swing at this because folks have said things that are true "except" and it is the exceptions that can get you into trouble. Is the panel you will be running your service from the main panel of sub panel? If main panel it is OK to run the neutral and ground to the same buss. However if it is a sub panel it is not OK to run them to the same buss, but the ground must go to the ground buss and neutral to the neutral buss.

The wire size for a 30 amp would be 10/3 plus ground. This is from Table 310-16 of the NEC found on page 70A-71 of the NFPA-70 for one and two family dwellings but taken from the NEC. If the unit is 20 amps or less it is OK to use the 12/3 with ground.

If you are going to run the wire and set the receptacle yourself a few things to remember, the wire going into the receptacle box must be secured with in 12" of the box. At the panel it must be secured with in 2' of the panel but must also be secured where it enters the panel with and approved clamping device (ask the guy at the box store) when securing the ground into the ground buss no more than 2 wires are permitted under a buss screw, however only one neutral wire is permitted per neutral bus that is code.

When you have run everything to the panel disconnect the main breaker. In newer houses it is sometimes located near the meter on older houses it is generally the large breaker at the top of the panel and will have some large number like 100 150 amps and so on. At his point it is save to install the new breaker and connect the wire to the proper buss or breaker. After securing all connections turn off the new breaker before turning on the main. Once the main is on reset the new breaker and if nothing happens that is good. Use an appropriate meter to check that the neutral and one hot wire have not been crossed. Check that the ground is in fact grounded properly in the device and in the main panel. Now plug in your new DC and make sawdust and tell us how it all went.

I have made this as not rocket science as I can, and for Lavon and John and myself it is very straight forward but if you have never messed inside the panel, set breaker and the like just be careful man, It may not be rocket science but it will kill you if you don't do it right so please be careful.

And if you already know all this then have at it.

Wisdom: Where experience and knowledge combine and become one.

"We are all one decision away from Stupid!!"

Lamentations 3:22-23

"How often we sacrifice the permanent plans of God on the altar of immediate solutions"

I have a very good memory, just short is all.
xplorx4 is offline  
post #9 of 112 (permalink) Old 07-28-2009, 08:27 PM
Registered User
 
levon's Avatar
 
Join Date: Sep 2008
Country: United States
First Name: levon
Posts: 1,820
 
Default

sorry, i stand corrected, if you dont secure the wire within 12" of the box and 2" of the panel your dc will not work. just teasing, it will work, but jerry was talking about code. i think jerry was an inspector.

light travels faster than sound, this is why some people seem bright til you hear them speak.

Please Please Please edit your profile with a name and location so we can better assist you and make for a friendlier forum

levon

Last edited by levon; 07-28-2009 at 08:47 PM.
levon is offline  
post #10 of 112 (permalink) Old 07-28-2009, 08:30 PM
Registered User
 
Cassandra's Avatar
 
Join Date: Mar 2006
Country: Canada
First Name: Cassandra
Posts: 787
 
Default

Hi Bob:

The Delta 50-850 (DeWALT ServiceNET - Official Online Store for DeWALT, Porter Cable, Delta, and Black and Decker Parts) is configurable for either 110V or 220V, as shown in the user manual at the link I provided.

One thing to note: they show the neutral being switched in the 110V circuit. Check your local electrical safety code -- some jurisdictions (such as Canada) do not allow switched neutrals. This is a safety issue.

Cassandra

Carpe diem, quam minimum credula postero
http://www.panoramio.com/user/5924351

Last edited by Cassandra; 07-28-2009 at 08:36 PM.
Cassandra is offline  
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Router Forums forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in











Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page
Display Modes
Linear Mode Linear Mode



Similar Threads
Thread Thread Starter Forum Replies Last Post
Blown Hitachi M12V speed control bypassed honyacker General Routing 13 04-22-2017 11:25 AM
Craftsman 315.240260 wiring question hgreer New Member Introductions 4 12-30-2008 09:34 PM
Freud speed control module pedixon New Member Introductions 12 02-27-2008 08:26 AM
Dewalt DW670 + speed control Thrifty Tool Guy Portable Routing 11 09-16-2007 07:42 AM
Remote Motor control bobj3 Lobby 0 01-04-2007 12:32 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome