Default Starting Current

Hi,

I will be buying a Bosch POF 1400 ACE router soon. I want to make sure the electrical circuit that will serve it is sized properly. At 220V the normal operating current will be 6-7 amps. Frequently, these types of machines have a high starting current but this is not mentioned in the manual. This high current, if it exists, could cause a trip if it is not designed for. Any thoughts? Thanks

May The Lord Give You Peace
Engine44 is offline  
Sponsored Links
Advertisement
 
post #2 of 10 (permalink) Old 03-21-2011, 11:12 AM
Registered User
 
Ralph Barker's Avatar
 
Join Date: Dec 2008
Country: United States
First Name: Ralph
Posts: 2,001
 
Default

The surge starting current on a non-soft-start motor can be in the range of 150% to almost 200% of the running current. It is, however, quite brief. Here in the U.S., anyway, the surge is over before the typical circuit breaker can react. I have no idea what the electrical standards are there, however.

- Ralph
Ralph Barker is offline  
post #3 of 10 (permalink) Old 03-21-2011, 07:21 PM
Registered User
 
Cassandra's Avatar
 
Join Date: Mar 2006
Country: Canada
First Name: Cassandra
Posts: 787
 
Default

Bob:

When we electrical engineers calculate the needed circuit breaker, a technique is to total the running currents of the loads on that circuit and add 1/4 of highest motor current on the circuit. This usually keeps one out of trouble with nuisance tripping of the circuit breaker.

For example, if you have router with a running current of 7 amps and a dust collector with a running current of 5 amps, the minimum circuit breaker rating is 7 + 5 + (7/4) amps. That's a load of 13.75 amps. So, a 15 amp breaker should be adequate, especially since the total running current is 12 amps, or 80 percent of a 15 amp breaker's rating.

A router with a soft-start takes less current during starting than a router with no soft-start. The calculations just given can still be applied, resulting in a greater margin from nuisance tripping.

Cassandra

Carpe diem, quam minimum credula postero
http://www.panoramio.com/user/5924351
Cassandra is offline  
Sponsored Links
Advertisement
 
post #4 of 10 (permalink) Old 03-21-2011, 08:48 PM
Forum Contributor
 
Join Date: Jan 2006
Country: United States
First Name: Bj
Posts: 23,786
       
Default

Hi Cassandra

I have a question for you ,I know you are sharp with this type of stuff. I have a vac. system 2HP (15 amp. pull )on a 20 amp.breaker and the 3 1/4 HP router (15amp) on the same breaker, on 10 ga. copper wire running from the panel to the outlet boxes, I just about always I fire up the Vac.system 1st.but not always and than the router and never pop the breaker, how can that be ?

=========

Quote:
Originally Posted by Cassandra View Post
Bob:

When we electrical engineers calculate the needed circuit breaker, a technique is to total the running currents of the loads on that circuit and add 1/4 of highest motor current on the circuit. This usually keeps one out of trouble with nuisance tripping of the circuit breaker.

For example, if you have router with a running current of 7 amps and a dust collector with a running current of 5 amps, the minimum circuit breaker rating is 7 + 5 + (7/4) amps. That's a load of 13.75 amps. So, a 15 amp breaker should be adequate, especially since the total running current is 12 amps, or 80 percent of a 15 amp breaker's rating.

A router with a soft-start takes less current during starting than a router with no soft-start. The calculations just given can still be applied, resulting in a greater margin from nuisance tripping.

Cassandra



"It's fine to disagree with other members as long as you respect their opinions"

Marc Sommerfeld Tools ,Videos
http://www.youtube.com/channel/UCT-n...RWaEpMA/videos

Find all threads started by bobj3
http://www.routerforums.com/search.php?searchid=944097



Last edited by bobj3; 03-21-2011 at 08:56 PM.
bobj3 is offline  
post #5 of 10 (permalink) Old 03-21-2011, 10:30 PM
Registered User
 
Cassandra's Avatar
 
Join Date: Mar 2006
Country: Canada
First Name: Cassandra
Posts: 787
 
Default

Quote:
Originally Posted by bobj3 View Post
Hi Cassandra

I have a question for you ,I know you are sharp with this type of stuff. I have a vac. system 2HP (15 amp. pull )on a 20 amp.breaker and the 3 1/4 HP router (15amp) on the same breaker, on 10 ga. copper wire running from the panel to the outlet boxes, I just about always I fire up the Vac.system 1st.but not always and than the router and never pop the breaker, how can that be ?

=========
Hi Bob:

It all comes down to what the numbers mean. If one throws an ammeter on the line to each piece of equipment, one is likely to see that neither the vacuum nor the router is actually drawing the amperage indicated on the label. Why?

Let's look at that 3-1/4 HP router. Routers tend to be rated in peak power or current. Peak is the operative word here. One would not normally push the router hard enough to sustain the peak current. Peak means one can push the router to this value without damage to the router. However, in most work, one wouldn't achieve peak.

Similarly, the vacuum will draw the 2 HP only under certain conditions. Most of the time, these conditions don't exist and the vacuum draws less power and current.

-----------------

So, let's say you have a 1/4" double-flute spiral bit in the router, and you're proceeding with making a groove in oak, at normal feed speed. What power is being taken? Definitely not the 3-1/4 HP. Probably below 1 HP.

Being the diligent worker, you don't allow the vacuum to struggle against a clogged bag and you empty the vacuum before it fills more than half way. Probably less than 1 HP draw.

Together you have less than 2 HP, which is less than the 20 amp breaker rating.

--------------------------

Another issue is that your router may have a soft-start, which limits the current on start-up. So, it's smart for one to start the vacuum before the router. The vacuum probably has the greater starting current.

Carpe diem, quam minimum credula postero
http://www.panoramio.com/user/5924351
Cassandra is offline  
post #6 of 10 (permalink) Old 03-21-2011, 10:44 PM
Forum Contributor
 
Join Date: Jan 2006
Country: United States
First Name: Bj
Posts: 23,786
       
Default

Hi

Thanks,,I have in the pass played with it by blocking off the hose on the Vac. to make it draw more at full load and push a Big panel bit at full cut and it did not pop the breaker.. just lucky I guess .. thanks


======

Quote:
Originally Posted by Cassandra View Post
Hi Bob:

It all comes down to what the numbers mean. If one throws an ammeter on the line to each piece of equipment, one is likely to see that neither the vacuum nor the router is actually drawing the amperage indicated on the label. Why?

Let's look at that 3-1/4 HP router. Routers tend to be rated in peak power or current. Peak is the operative word here. One would not normally push the router hard enough to sustain the peak current. Peak means one can push the router to this value without damage to the router. However, in most work, one wouldn't achieve peak.

Similarly, the vacuum will draw the 2 HP only under certain conditions. Most of the time, these conditions don't exist and the vacuum draws less power and current.

-----------------

So, let's say you have a 1/4" double-flute spiral bit in the router, and you're proceeding with making a groove in oak, at normal feed speed. What power is being taken? Definitely not the 3-1/4 HP. Probably below 1 HP.

Being the diligent worker, you don't allow the vacuum to struggle against a clogged bag and you empty the vacuum before it fills more than half way. Probably less than 1 HP draw.

Together you have less than 2 HP, which is less than the 20 amp breaker rating.

--------------------------

Another issue is that your router may have a soft-start, which limits the current on start-up. So, it's smart for one to start the vacuum before the router. The vacuum probably has the greater starting current.



"It's fine to disagree with other members as long as you respect their opinions"

Marc Sommerfeld Tools ,Videos
http://www.youtube.com/channel/UCT-n...RWaEpMA/videos

Find all threads started by bobj3
http://www.routerforums.com/search.php?searchid=944097


bobj3 is offline  
post #7 of 10 (permalink) Old 03-22-2011, 05:38 AM
Registered User
 
Cassandra's Avatar
 
Join Date: Mar 2006
Country: Canada
First Name: Cassandra
Posts: 787
 
Default

You're welcome, Bob!

Sometimes it's annoying. One might go months using a set-up and nothing happens. Then one day, one does the same thing and the breaker pops. "But I've doing this for months, what happened this time?" Nothing really, just one has been playing too close to the edge and went over this time.

Cassandra

Carpe diem, quam minimum credula postero
http://www.panoramio.com/user/5924351

Last edited by Cassandra; 03-22-2011 at 05:41 AM.
Cassandra is offline  
post #8 of 10 (permalink) Old 03-22-2011, 09:39 AM
gav
Registered User
 
Join Date: Oct 2009
Country: Croatia
First Name: Gavin
Posts: 777
 
Default

Quote:
Originally Posted by Engine44 View Post
Hi,

I will be buying a Bosch POF 1400 ACE router soon. I want to make sure the electrical circuit that will serve it is sized properly. At 220V the normal operating current will be 6-7 amps. Frequently, these types of machines have a high starting current but this is not mentioned in the manual. This high current, if it exists, could cause a trip if it is not designed for. Any thoughts? Thanks
Seeing as I have that exact router, I can safely say you won't have a problem as it has 'soft start'.
As an example, in the basement of my building there is a wall plug that is wired up to the lighting circuit. I have run my router off of it many times without the breaker tripping.
gav is offline  
post #9 of 10 (permalink) Old 03-22-2011, 01:59 PM
Registered User
 
Cassandra's Avatar
 
Join Date: Mar 2006
Country: Canada
First Name: Cassandra
Posts: 787
 
Default

Hi Gavin:

It is a good idea to keep power tools off the lighting circuits. If anything goes wrong with the tool and one is working late in the evening, one could easily be left in the dark.

My father's workshop had lights and receptacles on the same circuits. I re-wired the shop, using one circuit for the lights and two circuits for receptacles. No need to worry about a faulty tool leaving us in the dark.

Cassandra

Carpe diem, quam minimum credula postero
http://www.panoramio.com/user/5924351
Cassandra is offline  
post #10 of 10 (permalink) Old 03-22-2011, 02:20 PM
gav
Registered User
 
Join Date: Oct 2009
Country: Croatia
First Name: Gavin
Posts: 777
 
Default

I know Cassandra, but at the time I didn't have a choice. The building I live in is quite old and the wiring leaves a lot to be desired. Even some of the plugs in my apartment are on a lighting circuit.
I now have a workshop with proper wiring, even 3 phase, which I have no need for as yet.
gav is offline  
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Router Forums forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in











Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page
Display Modes
Linear Mode Linear Mode



Similar Threads
Thread Thread Starter Forum Replies Last Post
Starting with a router Knothead47 General Routing 7 02-23-2010 07:06 PM
Just starting out rx3584 New Member Introductions 4 03-27-2009 05:59 PM
Outlook Express problems BrianS Lobby 6 01-06-2008 07:23 AM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome