Hi, I have a pretty straightforward question. How easy would it be to route a 13mm channel into chipboard to accept a 12mm pipe for underfloor heating?

The catch is I would need to cut an overall length of 100M plus. Is this plausible? Is there a bit that would be able to handle it?

Many thanks

Mark
moneymark is offline  
Sponsored Links
Advertisement
 
post #2 of 11 (permalink) Old 09-03-2015, 02:34 PM
Registered User
 
MAFoElffen's Avatar
 
Join Date: Jun 2012
Country: United States
First Name: Mike
Posts: 2,369
 
Default

For 100 meters???

If it were me and we were talking for underfloor radiant heating lines... I would mark it out > Set your depth of cut on your circular saw. Cut the outline with a circular saw. Cut bend outlines with a kick saw. Cut a few between those boundaries and chip it out with a pry bar. (usually cuts spaced about 1/8"-1/4" apart and all that just pried out)

Why? Chipboard particles and glue are hard on tooling. 100 meters is a ways. For installation of tubing for heating, it is not rocket science. You do not need a precision channel. For an installer, you are paid for the job, not by the hour. The precision of the channel profile does not affect the transfer of heat and it is not something that is seen.

But from what you are describing and the way you are describing it... don't you need to re-look at your design and how radiant systems are installed? I'm no expert on these, but...

You're filling the channels for your PEX tubing for your radiant heat system with screed right? (so a channel for a 12mm PEX is usually bigger than just 13mm...) And above that probably some thin screed board? It's the screed that helps transfer the heat from the tubing and spread that heat transfer out to a full surface... Instead of just where your coils are (directly). The heat transfer of wood or particle board is not as efficient as screed.

Most installers just use tubing guides on top the base (sort of looks like a comb) , the tube laid in the guides to hold them in place, the screed layer (that then surrounds the tubes), then cover that with the floor... not even fooling with cutting channels (where channels are going to weaken an existing structures subfloor).. Do you have a height requirement/limitation where you need to have channels cut into the subfloor?
Murtu01 likes this.

"Don't worry, I saw this work in a cartoon once."
"Usually learning skills and tooling involves a progression of logical steps."

Last edited by MAFoElffen; 09-03-2015 at 02:54 PM.
MAFoElffen is offline  
post #3 of 11 (permalink) Old 09-03-2015, 02:47 PM
Registered User
 
hawkeye10's Avatar
 
Join Date: Jul 2015
Country: United States
First Name: Don
Posts: 2,603
 
Default

I don't know a whole lot and could be very wrong, but isn't it a bad idea to have chip board in a floor? If water ever got to it the chip board would swell and buckle bad.
MT Stringer likes this.

Don in Murfreesboro,Tn.

Measure once cut twice and it's still to short.
hawkeye10 is offline  
Sponsored Links
Advertisement
 
post #4 of 11 (permalink) Old 09-03-2015, 03:04 PM
Registered User
 
MAFoElffen's Avatar
 
Join Date: Jun 2012
Country: United States
First Name: Mike
Posts: 2,369
 
Default

Fairly standard in the last 20 years. Even for roof decking and outside sheathing (OSB). OSB is not "particle" board. OSB stands for Oriented Strand Board. The strands are oriented, glued and compressed into shaped. The glue used makes it a good choice for exterior work. (Within reason.)

You have to remember that even ply products are glued laminates. A lot has to do with the layers and the glues used. TJI trus joists are the same OSB material in the web with laminate ribs.

"Don't worry, I saw this work in a cartoon once."
"Usually learning skills and tooling involves a progression of logical steps."

Last edited by MAFoElffen; 09-03-2015 at 03:13 PM.
MAFoElffen is offline  
post #5 of 11 (permalink) Old 09-03-2015, 05:05 PM
Registered User
 
hawkeye10's Avatar
 
Join Date: Jul 2015
Country: United States
First Name: Don
Posts: 2,603
 
Default

Quote:
Originally Posted by MAFoElffen View Post
Fairly standard in the last 20 years. Even for roof decking and outside sheathing (OSB). OSB is not "particle" board. OSB stands for Oriented Strand Board. The strands are oriented, glued and compressed into shaped. The glue used makes it a good choice for exterior work. (Within reason.)

You have to remember that even ply products are glued laminates. A lot has to do with the layers and the glues used. TJI trus joists are the same OSB material in the web with laminate ribs.
Thanks Mike I didn't understand it was OSB.

Don in Murfreesboro,Tn.

Measure once cut twice and it's still to short.
hawkeye10 is offline  
post #6 of 11 (permalink) Old 09-03-2015, 05:15 PM
Moderation Team
 
MT Stringer's Avatar
 
Join Date: Aug 2012
Country: United States
First Name: Mike
Posts: 5,644
 
Default

100 meters?
I'd like to see pics of this house.

That's my story and I'm stickin' to it!
MT Stringer is online now  
post #7 of 11 (permalink) Old 09-03-2015, 05:15 PM Thread Starter
Registered User
 
Join Date: Sep 2015
Country: United States
First Name: N/a
Posts: 3
 
Default

Thanks for the replies. I've been reading more into it and I think I'm probably over complicating things.

I'm going to go the more traditional route and put the pipe over the insulation and lay the floor above.

Not sure if I'm going to screed yet. I've heard that if you seal the insulation with expanding foam to get everything air tight it can eliminate the need to screed.
moneymark is offline  
post #8 of 11 (permalink) Old 09-03-2015, 10:17 PM
Registered User
 
MAFoElffen's Avatar
 
Join Date: Jun 2012
Country: United States
First Name: Mike
Posts: 2,369
 
Default

Quote:
Originally Posted by MT Stringer View Post
100 meters?
I'd like to see pics of this house.
Answer to Mike (MT):

If you look at a normal layout (above), 100 meters is around 328 feet... You can see by a layout diagram that it would be easy to layout that much PEX, in a zone in a normal sized house right?

But planning a radiant heat heating zone, 12mm Pex (or 1/2" PEX here), has a min run length of 100 feet and Max length run of 300 feet (in one zone). Longer than that and your heat starts dropping off too much. At 1/2" PEX, you have a radius/spacing of 6"-8".

So 100 meters is just over the limit length of 1/2" PEX... (For a single zone.) That would be where above they split a living room into 2 zones, because it was too much length for just one.

If you plan a larger zone with a longer run (200-400 feet) then you can go 7/8" PEX with a radius/spacing of 12"-16". If you have 150" total or less, you can go 3/8 PEX.
MT Stringer likes this.

"Don't worry, I saw this work in a cartoon once."
"Usually learning skills and tooling involves a progression of logical steps."
MAFoElffen is offline  
post #9 of 11 (permalink) Old 09-03-2015, 10:36 PM
Moderation Team
 
Cherryville Chuck's Avatar
 
Join Date: Sep 2010
Country: Canada
First Name: Charles
Posts: 15,082
 
Default

Quote:
Originally Posted by moneymark View Post
Thanks for the replies. I've been reading more into it and I think I'm probably over complicating things.

I'm going to go the more traditional route and put the pipe over the insulation and lay the floor above.

Not sure if I'm going to screed yet. I've heard that if you seal the insulation with expanding foam to get everything air tight it can eliminate the need to screed.
I'm not sure what you mean by insulating to eliminate screed but the idea of in floor hydronic heating is to transfer the heat to a large thermal mass. The large mass retains heat for a long period of time once it is warmed up and is also slow to change temperature which makes it more comfortable than forced air systems for example where it cycles from low to high and back again. The last thing you would want to do is insulate the piping from the thermal mass.

Someone I consider a master woodworker once told me that a master woodworker is not someone who never makes mistakes. He is someone who is able to cover them up so that no one can tell.
Cherryville Chuck is online now  
post #10 of 11 (permalink) Old 09-04-2015, 12:12 AM
Moderation Team
 
MT Stringer's Avatar
 
Join Date: Aug 2012
Country: United States
First Name: Mike
Posts: 5,644
 
Default

Quote:
Originally Posted by MAFoElffen View Post
Answer to Mike (MT):

If you look at a normal layout (above), 100 meters is around 328 feet... You can see by a layout diagram that it would be easy to layout that much PEX, in a zone in a normal sized house right?

But planning a radiant heat heating zone, 12mm Pex (or 1/2" PEX here), has a min run length of 100 feet and Max length run of 300 feet (in one zone). Longer than that and your heat starts dropping off too much. At 1/2" PEX, you have a radius/spacing of 6"-8".

So 100 meters is just over the limit length of 1/2" PEX... (For a single zone.) That would be where above they split a living room into 2 zones, because it was too much length for just one.

If you plan a larger zone with a longer run (200-400 feet) then you can go 7/8" PEX with a radius/spacing of 12"-16". If you have 150" total or less, you can go 3/8 PEX.
Ah ha! I see the light said the blind man. Never thought about it like that. Don't see much of that where I live. Thanks for 'splainin' it.

That's my story and I'm stickin' to it!
MT Stringer is online now  
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Router Forums forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in











Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page
Display Modes
Linear Mode Linear Mode



Similar Threads
Thread Thread Starter Forum Replies Last Post
Forum Suggestion Thread Mark Site Help and Suggestions 131 02-08-2015 10:33 AM
Routing Tutorials ModeratorTeam Guide Bushings and Templates 4 02-01-2015 09:37 AM
old person new to routing in wood sailer670 New Member Introductions 12 12-13-2014 08:31 PM
Use of template Guides cutter79 Guide Bushings and Templates 6 08-21-2013 04:18 AM
CNC routing as first routing experience ianthehenry CNC Routing 23 04-25-2012 05:24 AM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome