Angry 220 Volt Extension Cords

I have recently acquired a used Delta Unisaw with a 3HP 220 Volt motor and the cord on the saw ends about 10-15 feet from a new 220 Volt dedicated outlet served by a 30 amp circuit breaker. I believe the cord on the Unisaw has the original plug. How long an extension cord can I use and what wire gauge would be required to safely serve the Unisaw? Any help in setting this up safely would be appreciated.
jbullockusanet is offline  
Sponsored Links
Advertisement
 
post #2 of 56 (permalink) Old 03-12-2014, 04:29 PM
Registered User
 
DaninVan's Avatar
 
Join Date: Dec 2011
Country: Canada
First Name: Dan
Posts: 13,765
 
Default

30 Amp breaker requires #10 ga wiring, John. In theory you could probably run the motor with a 12 ga cord, because it's relatively short, but if you're fortunate enough to have a 3HP/220V beast of a motor, why would you want to handicap it with inadequate wiring. Obviously you don't; that's why you're asking!
The motor probably draws 21+ amps?
DaninVan is offline  
post #3 of 56 (permalink) Old 03-12-2014, 08:47 PM
Registered User
 
Dejure's Avatar
 
Join Date: Jul 2009
Country: United States
First Name: Kelly
Posts: 613
 
Default

There is an old rule in electronics, which is that you can always run bigger wire, but you cannot run smaller wire. In short, it will not hurt a thing if you run "too big an extension cord" to your saw.

My 3hp Unisaw, and the one before it, will run fine on 12 gauge circuits (20 amp), but I ran 10 gauge to them because I'm just that way. I like the "extra amp room"and I believe it's a good practice.

If you are running ten gauge extension cord, you should be able to run it the same as you would hard wire 10 gauge, if not more. I suspect even twelve gauge multi-strand could run a long way. The weak point would be your connections. Simply put, if you are not generating heat in the line, you're okay.

I have a generator I run to a five conductor 8 gauge. I tied leads together and made it into a monster, 100' foot extension I'd run even the Unisaw from. Of course, the gen wouldn't appreciate it.



Quote:
Originally Posted by jbullockusanet View Post
I have recently acquired a used Delta Unisaw with a 3HP 220 Volt motor and the cord on the saw ends about 10-15 feet from a new 220 Volt dedicated outlet served by a 30 amp circuit breaker. I believe the cord on the Unisaw has the original plug. How long an extension cord can I use and what wire gauge would be required to safely serve the Unisaw? Any help in setting this up safely would be appreciated.

The reason I have what you want is, I never lent it out before.

Scraps are a myth.

Last edited by Dejure; 03-12-2014 at 10:00 PM.
Dejure is offline  
Sponsored Links
Advertisement
 
post #4 of 56 (permalink) Old 03-12-2014, 11:34 PM
Moderation Team
 
Cherryville Chuck's Avatar
 
Join Date: Sep 2010
Country: Canada
First Name: Charles
Posts: 14,763
 
Default

I also have a unisaw and would go with the 10 gauge. Your uni came with a plug? Mine didn't. In fact, I think it only came with the wire from the switch to the motor. I don't remember a power wire.

Someone I consider a master woodworker once told me that a master woodworker is not someone who never makes mistakes. He is someone who is able to cover them up so that no one can tell.
Cherryville Chuck is offline  
post #5 of 56 (permalink) Old 03-13-2014, 07:05 AM
Registered User
 
IC31's Avatar
 
Join Date: Nov 2012
Country: United States
First Name: Dave W
Posts: 500
 
Default

I would use an RV 30 amp extension cord then install a companion wall outlet along with a plug on the saw wire. This RV extension cord is 10 ga, very robust as far as insulation and fairly flexible to get it out of the way It would probably be way too long (usually 20 to 35 feet), but can alternatively be used for a generator or a 30 amp RV if you have one.

Dave W

Quando omni flunkus, moritati (When all else fails, play dead - R Green)
IC31 is offline  
post #6 of 56 (permalink) Old 03-13-2014, 09:18 AM
Registered User
 
Gene Howe's Avatar
 
Join Date: Jul 2007
Country: United States
First Name: Gene
Posts: 9,283
 
Default

Dave has a great idea. But, if you're not going to be moving it often, why not just wire a new RV cord direct to the motor and forget the extension cord aspect.

Gene Howe
Snowflake, AZ

'The true soldier fights not because he hates what is in front of him, but because he loves what is behind him.' G. K. Chesterton

Please edit your profile with a name and location so we can better assist you and make for a friendlier forum.
Gene Howe is offline  
post #7 of 56 (permalink) Old 03-13-2014, 10:13 AM
Registered User
 
Join Date: Mar 2010
Country: United States
First Name: Nick
Posts: 5
 
Default

That is the best choice dont use the extension you have to make the cord anyway just go straight to the motor and 10 gage wire is more than u probably need but you loose less current on a long run with heavier wire.
Blackcloud is offline  
post #8 of 56 (permalink) Old 03-13-2014, 10:33 AM
Registered User
 
Dejure's Avatar
 
Join Date: Jul 2009
Country: United States
First Name: Kelly
Posts: 613
 
Default

I have to vote with the others - a longer cord would be best, if it's a long term install where it's at. Again, each connection is a voltage drop potential.

The RV cord is fine, but you can buy the cord and plug at a big box or an electrical supply and would probably save money. The RV cord will have to have the male end chopped off and they can add a lot to cost.

Your current cord is probably only three conductor, but you can use a four conductor when you replace it, to add a frame ground. Just for reference, both my right and my left tilt Unisaws came with cords and plugs and, as noted, were three conductor.

As I mentioned, I could get by with a 12 gauge (20 amp. That is what comes on the 3hp saws and all it calls for, but ten gauge leaves room for a bigger motor or using the cord on other equipment.

_____________________________________
Comments from the Amazon pages:

From the manual: "A suitable circuit should not be less than AWG 12/3 wiring..." (for 3hp single phase). Such a circuit requires a 20 amp dbl. pole breaker.
Thomas O. answered on October 23, 2013

Comment | 1 of 1 found this helpful. Do you? | Report abuse
220-240 volt and minimum 15 amp circuit. The plug is for a 15 amp 230 volt outlet so that's the minimum. This is for the 3HP motor.
Gauda answered on October 23, 2013

Comment | Do you find this helpful? | Report abuse
The 3 Hp saw comes prewired with a 20 Amp 3 prong 220V plug. The saw will draw about 12.4 amps running. Use a 20 Amp 220V circuit with a minimum 12 gauge line wiring.
Mike answered on October 24, 2013

Comment (1) | Do you find this helpful? | Report abuse
I run it with 240v dedicated 20 amp double pole breaker. I also use a heavy duty, 10/3, 25 foot extension cord to reach the saw.
GlenT answered on October 24, 2013

The reason I have what you want is, I never lent it out before.

Scraps are a myth.
Dejure is offline  
post #9 of 56 (permalink) Old 03-13-2014, 12:44 PM
Moderation Team
 
Cherryville Chuck's Avatar
 
Join Date: Sep 2010
Country: Canada
First Name: Charles
Posts: 14,763
 
Default

That type saw isn't meant to be moved and I didn't intend to move mine again once I had it set up so I wired it direct to my panel using armored BX cable. Unless you have yours set up so that the cord will never be stepped on then I would recommend that it be done that way. You'll never have to replace it or worry about a short circuit from wires rubbing together.

Someone I consider a master woodworker once told me that a master woodworker is not someone who never makes mistakes. He is someone who is able to cover them up so that no one can tell.
Cherryville Chuck is offline  
post #10 of 56 (permalink) Old 03-14-2014, 02:27 AM
Registered User
 
MAFoElffen's Avatar
 
Join Date: Jun 2012
Country: United States
First Name: Mike
Posts: 2,369
 
Default

Mine is overkill. 6 gauge wire to one of 4 240volt outlets in my garage (2 30 amp oulets and 2 50 amp outlets). The panel saw I have to a 50 amp and use the same connectors as my welders. For my welders, I have a 50 foot 2 gauge (angel hair) extension cord (600volt). (<-- I picked up the coil at a garage sale for $20!)

I have a 1300# plus saw but opted to run flexible cables that could be disconnected. Why you ask? It's not like I can drag that saw out to the end of the driveway to use, so it's not that...

Because my saw is set in the middle of the garage. There is the working room required to do different things... It moves against a wall (right side) when I need the extra space. When I have to break down sheets, I need to move it from the wall so I can get a full sheet of movement. I havew to move things from behind it if I need full movement of the table.

The much bigger factor is that I have "other" very heavy things I have to get around my saw and I would be not able to get them safety over an armored cable.

"Don't worry, I saw this work in a cartoon once."
"Usually learning skills and tooling involves a progression of logical steps."

Last edited by MAFoElffen; 03-14-2014 at 04:25 PM.
MAFoElffen is offline  
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Router Forums forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in











Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page
Display Modes
Linear Mode Linear Mode



Similar Threads
Thread Thread Starter Forum Replies Last Post
220 volt Router plunge eddy sastra New Member Introductions 4 02-22-2014 09:06 PM
1615evs 220 volt need help bentwood General Routing 4 12-10-2013 01:43 PM
Bosch 1615evs in 220 volt bentwood New Member Introductions 21 12-10-2013 12:35 AM
Bosch 220 volt router help jimh48 Table-mounted Routing 7 02-15-2013 09:28 AM
Does anybody know of a 220 volt (motor only) router? lowcrust Table-mounted Routing 27 08-31-2012 10:25 AM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome