220 Volt Extension Cords

22K views 55 replies 13 participants last post by  RainMan 2.0  
#1 ·
I have recently acquired a used Delta Unisaw with a 3HP 220 Volt motor and the cord on the saw ends about 10-15 feet from a new 220 Volt dedicated outlet served by a 30 amp circuit breaker. I believe the cord on the Unisaw has the original plug. How long an extension cord can I use and what wire gauge would be required to safely serve the Unisaw? Any help in setting this up safely would be appreciated.:moil:
 
#2 ·
30 Amp breaker requires #10 ga wiring, John. In theory you could probably run the motor with a 12 ga cord, because it's relatively short, but if you're fortunate enough to have a 3HP/220V beast of a motor, why would you want to handicap it with inadequate wiring. Obviously you don't; that's why you're asking! :)
The motor probably draws 21+ amps?
 
#3 · (Edited)
There is an old rule in electronics, which is that you can always run bigger wire, but you cannot run smaller wire. In short, it will not hurt a thing if you run "too big an extension cord" to your saw.

My 3hp Unisaw, and the one before it, will run fine on 12 gauge circuits (20 amp), but I ran 10 gauge to them because I'm just that way. I like the "extra amp room"and I believe it's a good practice.

If you are running ten gauge extension cord, you should be able to run it the same as you would hard wire 10 gauge, if not more. I suspect even twelve gauge multi-strand could run a long way. The weak point would be your connections. Simply put, if you are not generating heat in the line, you're okay.

I have a generator I run to a five conductor 8 gauge. I tied leads together and made it into a monster, 100' foot extension I'd run even the Unisaw from. Of course, the gen wouldn't appreciate it.
 
#4 ·
I also have a unisaw and would go with the 10 gauge. Your uni came with a plug? Mine didn't. In fact, I think it only came with the wire from the switch to the motor. I don't remember a power wire.
 
#5 ·
I would use an RV 30 amp extension cord then install a companion wall outlet along with a plug on the saw wire. This RV extension cord is 10 ga, very robust as far as insulation and fairly flexible to get it out of the way It would probably be way too long (usually 20 to 35 feet), but can alternatively be used for a generator or a 30 amp RV if you have one.
 
#6 ·
Dave has a great idea. But, if you're not going to be moving it often, why not just wire a new RV cord direct to the motor and forget the extension cord aspect.
 
#8 ·
I have to vote with the others - a longer cord would be best, if it's a long term install where it's at. Again, each connection is a voltage drop potential.

The RV cord is fine, but you can buy the cord and plug at a big box or an electrical supply and would probably save money. The RV cord will have to have the male end chopped off and they can add a lot to cost.

Your current cord is probably only three conductor, but you can use a four conductor when you replace it, to add a frame ground. Just for reference, both my right and my left tilt Unisaws came with cords and plugs and, as noted, were three conductor.

As I mentioned, I could get by with a 12 gauge (20 amp. That is what comes on the 3hp saws and all it calls for, but ten gauge leaves room for a bigger motor or using the cord on other equipment.

_____________________________________
Comments from the Amazon pages:

From the manual: "A suitable circuit should not be less than AWG 12/3 wiring..." (for 3hp single phase). Such a circuit requires a 20 amp dbl. pole breaker.
Thomas O. answered on October 23, 2013

Comment | 1 of 1 found this helpful. Do you? | Report abuse
220-240 volt and minimum 15 amp circuit. The plug is for a 15 amp 230 volt outlet so that's the minimum. This is for the 3HP motor.
Gauda answered on October 23, 2013

Comment | Do you find this helpful? | Report abuse
The 3 Hp saw comes prewired with a 20 Amp 3 prong 220V plug. The saw will draw about 12.4 amps running. Use a 20 Amp 220V circuit with a minimum 12 gauge line wiring.
Mike answered on October 24, 2013

Comment (1) | Do you find this helpful? | Report abuse
I run it with 240v dedicated 20 amp double pole breaker. I also use a heavy duty, 10/3, 25 foot extension cord to reach the saw.
GlenT answered on October 24, 2013
 
#9 ·
That type saw isn't meant to be moved and I didn't intend to move mine again once I had it set up so I wired it direct to my panel using armored BX cable. Unless you have yours set up so that the cord will never be stepped on then I would recommend that it be done that way. You'll never have to replace it or worry about a short circuit from wires rubbing together.
 
#10 · (Edited)
Mine is overkill. 6 gauge wire to one of 4 240volt outlets in my garage (2 30 amp oulets and 2 50 amp outlets). The panel saw I have to a 50 amp and use the same connectors as my welders. For my welders, I have a 50 foot 2 gauge (angel hair) extension cord (600volt). (<-- I picked up the coil at a garage sale for $20!)

I have a 1300# plus saw but opted to run flexible cables that could be disconnected. Why you ask? It's not like I can drag that saw out to the end of the driveway to use, so it's not that...

Because my saw is set in the middle of the garage. There is the working room required to do different things... It moves against a wall (right side) when I need the extra space. When I have to break down sheets, I need to move it from the wall so I can get a full sheet of movement. I havew to move things from behind it if I need full movement of the table.

The much bigger factor is that I have "other" very heavy things I have to get around my saw and I would be not able to get them safety over an armored cable.
 
#11 ·
John I built an extension cord for my table saw and my jointer. Both work on 220 volt circuits. I ran my wiring into a metal square D box and then enclosed the Square D box in a wooden box made from plywood.

I would recommend the twist lock connectors. These connectors are more money but it will not pull out of the wall and last a long time. If you want I can send you a few photos of mine. If your interested just PM me and I can email the photos and explained how I did it.

I have an old post which I think I posted what I did. Have a look and if you have anymore questions just PM me. http://www.routerforums.com/workshop-showroom/14498-garage-overall-shop.html
 
#12 ·
It's been niggling at me since John originally posted his question...
"...from a new 220 Volt dedicated outlet served by a 30 amp circuit breaker."

The beginning and end of the discussion is the 30AMP breaker part. Everything downstream must be rated 30AMP. That's the Electrical Code.
The motor rating is a red herring.
 
#18 ·
Coincidentally, I just ran into a very similar issue at our place, over the weekend. I've had a problem with our Beam built in vacuum shutting off on its own on occasion.
I replaced the whole motor unit (the machine minus the piping) last year because the old one was doing the same thing. I found the manual and went through it looking for some answers. Buried in there is the electrical instructions...the wiring must be 12/2 and the cct. breaker 20AMPS...of course the machine comes complete with a 15AMP cord and plug assembly!
When a new home is built, the Electrical Contractor is told to put in a cct. and receptacle for a b.i. vacuum, but isn't given any specs because at that point it's not likely that one has even been decided on. So what does he do? he wires in a dedicated 15 AMP cct. complete with a normal duplex receptacle. And when the vacuum arrives, the installer simply plugs it in, no questions asked.
 
#19 ·
Interesting Dan. I also have a Beam which I installed myself and I didn't see that in the manual either, but I did see the 15 amp plug and it worked fine for 15 years. However, last summer when I went home it would cut out after about 30 seconds. I think it might be a bad bearing but I'll have to remember to check that. They are supposed to be warrantied for life if I remember right, did you get free replacement?
 
#20 ·
I cannot imagine ever installing less than 12 gauge to an outlet. The only exception I've made is receptacles dedicated to lights and that are well marked. People shouldn't have to open an outlet or go to a fuse panel to determine its capacity. They should be able to presume them capable of twenty amps.

I see nothing wrong, in many instances, with running a 12 gauge extension cord in to a ten gauge circuit, a fourteen into a twelve gauge and so forth. Part of the reason for running a heavier gauge is to address the matter of the length of the run.

Several of my larger tools run relatively light cords. For example, my three horse Unisaw and my three horse dust collectors both run twelve gauge power cords, since they only draw about seven amps, after start up.
 
#21 ·
Kelly, I have no problem with that, in concept, except that the 20AMP wiring presumably has a 20 AMP breaker, Therefor it also requires a 20 amp receptacle, or a 20 AMP rated receptacle with a combination 15 and 20 AMP configuration.
Neither of those are found in the bargain bin.
I absolutely agree with you about the shop wiring being 20 AMP per cct.
 
#22 · (Edited)
Kelly

You hit the nail on the head in regards to what the electrical draw is on startup. I have a General Contractor tablesaw that is about 12 years old now. It came wired for 110 volts but can be wired for 220 volts. When I took the motor housing off the diagram showed me exactly what wires to change. The electrical draw in ampres was cut in half when I re-wired the saw to 220volts. This translates into drawing only 7.5 amps now compared with the initial 15 amps when it was wired for 110 volts.

When I wired the shop I went with (2) 20 ampre circuits along both walls and I am sure glad I did. The only 15 amp circuit I have is for the lights. I have (2) circuits for 220 volt in the wall for the dust collection and jointer. I have another 30 amp circuit for a welder.

The Canadian Electrical Code is a minimum and you can always over build and it won't hurt ... well just the pocket book maybe!

The only problem in not matching the wiring to the circuit breaker is if the load does increase to the full 20 ampres and you have just 14 gauge wiring this produces a chance of over heating the wire and thus causing a fire. I am not an electrician but I think that is the reason. It only makes sense right?
 
#23 ·
The only problem in not matching the wiring to the circuit breaker is if the load does increase to the full 20 ampres and you have just 14 gauge wiring this produces a chance of over heating the wire and thus causing a fire. I am not an electrician but I think that is the reason. It only makes sense right?
That is correct Dan. I'm not an electrician either but I've done all my own for the last 40 years. In BC, and I think Alberta is the same, you are allowed to take out a permit to do your own wiring as long as you do the work yourself and it gets inspected after, usually more diligently than a licensed electrician gets inspected. Dan in Van is correct that if it is to meet code, a 20 amp breaker must use 12 gauge wire and must be connected to a special receptacle. The standard duplex plug that you pick up at the hardware store for a buck cannot be used. Leviton | 20 Amp Duplex Receptacle, Ivory | Home Depot Canada
 
#24 ·
However, if it were that we had to match power cords to permanent wiring, we'd have to toss every one of our power supplies for printers, phones, radio and television power supply cords and so forth. MORE IMPORTANT, our shops would be affected. We'd have to change power cords on drills, routers. . . .
 
#26 ·
Keyyy; online discussions suggest that the Canadian Electrical Code is more rigid on this application than the US (ie you guys get a little more leeway in the interpretation.
The simple fact is that virtually all lighting and receptacle wiring up here is done with #14 and the breakers are 15AMP. Why, you ask? Because it's way cheaper.
NMD-90 Electrical Wire | RONA (that's approx. 250+')
Wire - Construction Wire | RONA
On top of the cable, there's the issue of how many wires are allowed in an outlet box, and the cost of 20Amp rated receptacles. Just not going to happen in residential construction; they're always looking for ways to reduce costs, not make it more expensive. All of the above doesn't mean that 20Amp ccts. wouldn't be a good idea. That's how I wired my own shop. As I've mentioned in the past, a 15 Amp breaker won't hold my compressor if I'm using it for high demand applications.

12 outets (mixed lts. and plugs) allowed per 15Amp cct.
 
#28 · (Edited)
Been called worse and, what the heck, when I was in law, I used an alias much of the time.

Was out in the shop and inspected the tag on the motor of the 3 hp Jet collector I bought last month. It says 25 AMPS!!! The 3 horse Unisaw runs at 7. Both motors are the same size. As such, it appears there is a huge winding quality difference.

Now I remember why I run 10 gauge to my 220 circuits.


I presume the rigid codes still allow heavier wire than required. Electrical laws of nature don't change. As such, I'd spend the extra for twelve to outlets because, sooner or later, someone is going to run a heater, or a microwave and a toaster, or..............
 
#30 ·
You have a very well equipped shop, Kelly!
I have heard that there are even some with TV, fridge and lounge chairs......ROTFL