Discussion Starter · #1 ·
Huanyang inverter model HY02D223B
Having issues with Spindle not reaching full RPM of 24000. Topping at 19200. Backstory here is I probably screwed something up in the wiring after switching my 2 spindles doing some troubleshooting. Before that I didn't have this issue. Any help or guidance is very much appreciated. 馃嵒
Gadget Audio equipment Electrical wiring Gas Electronic device
 

Registered
Joined
621 Posts
Q1.. Are you NOW controlling the VFD at it's console or externally via CNC Software?
Q2. The wirings to the Spindle is NOW correct?

If you can still program the VFD at it's console, I would just do a factory reset.

Answer Q1 and Q2 FIRST and I will post the parameter to change to do a FACTORY RESET.
 

Registered
Joined
9 Posts
Discussion Starter · #8 ·
Normal circumstances, and still now for most part I'm using software. Motion Force 19.10.0. I'm messing with the parameters manually. Lot of trial and error. Pretty dadgum neat though.

I'm 95 percent certain they are correct. I've gone back 3 times make sure. Rewired once. Just funny thus issue popped up after I messed with it.馃く
 

Registered
Joined
9 Posts
Discussion Starter · #9 ·
Normal circumstances, and still now for most part I'm using software. Motion Force 19.10.0. I'm messing with the parameters manually. Lot of trial and error. Pretty dadgum neat though.

I'm 95 percent certain they are correct. I've gone back 3 times make sure. Rewired once. Just funny thus issue popped up after I messed with it.馃く
@reuelt
 

Registered
Joined
621 Posts
MIB photon
If you are controlling by Computer program, how is the wiring from Computer to VFD?
Q3. Via 0-10V analog or Via MODBUS?

Don't do a factory reset YET since you are controlling via software.

19,200 could be just setting to 50Hz instead of 60Hz in USA.
50/60* 24000 = 20,000.

OR
If using 0-10V control - getting 8V instead of 10V.
 

Registered
Joined
120 Posts
You've got one or two of the settings wrong in the VFD. You have R, S, T for the 220V, and U, V, W, for the spindle itself plus grd. So if the spindle is working properly on/off, plus correct direction then everything is wired correctly. If you do a RESET then you'll have to re-program the VFD from the beginning.
 

Registered
Joined
9 Posts
Discussion Starter · #14 ·
You've got one or two of the settings wrong in the VFD. You have R, S, T for the 220V, and U, V, W, for the spindle itself plus grd. So if the spindle is working properly on/off, plus correct direction then everything is wired correctly. If you do a RESET then you'll have to re-program the VFD from the beginning.
I got me new spindles in today. I have to replace 1 minimum. I'll go through settings again 1x1. Thanks.
 