Default How safe is this power configuration?

I have a regular 2 socket, 15 amp outlet in my garage. I need to run my miter saw and shopvac at the same time, the saw draws 15A and the shopvac 8.5A.

I've currently been running them off one outlet through a 50 foot 14AWG extension cord with a 3 way splitter at the end. The other socket is running to a power strip by an extension cord that is powering by workbench light.

I know very little about electricity and it's boundaries, how bad is my current set up? What risks are there with this?

-Zach

Pax vobiscum
zm15 is offline  
Sponsored Links
Advertisement
 
post #2 of 23 (permalink) Old 06-13-2014, 08:53 PM
Registered User
 
Join Date: Jun 2011
Country: United States
First Name: Duane
Posts: 1,709
 
Default

Obviously, Zach, if both devices are a full load amps(FLA) you will trip the breaker if it is 15A. The miter saw will rarely hit the full 15A rated though. As you likely only run the miter saw a few seconds at a time, you may well get by with the situation.

That said, there would be less chance of tripping the breaker if both unit ran on separate circuits.

If both units ran at FLA for any period of time, and the breaker doesn't trip, then there is a likelyhood of overheating the wire and even possibly causing a fire.

I have found that hand tools are the best choice when I want to make mistakes at a slower rate of speed.

I don't suffer from insanity. I enjoy every minute of it.
Dmeadows is offline  
post #3 of 23 (permalink) Old 06-13-2014, 09:41 PM Thread Starter
Registered User
 
Join Date: Dec 2013
Country: United States
First Name: Zach
Posts: 40
 
Default

While it hasn't tripped the breaker yet, the lights do dim briefly when i run the saw, even if only the saw is plugged into the outlet. At what point does the saw actually hit 15 amps?

I don't have another receptacle (outlet) near the saw, i may have to have an electrician put one in.

Is it OK to power the saw over an extension cord like that provided its the right gauge?

-Zach

Pax vobiscum
zm15 is offline  
Sponsored Links
Advertisement
 
post #4 of 23 (permalink) Old 06-13-2014, 10:31 PM
Marine Engineer
 
kp91's Avatar
 
Join Date: Sep 2004
Country: United States
First Name: Doug
Posts: 4,684
 
Default

With extension cords, heavier gage is better. I would look for a 12 ga cord for that saw over that distance. Current is a unit of 'electron flow', so you want as big of a pipe (conductor) as possible, and as short of a run as necessary. Using a long light gage extension cord could cause the impedance in the circuit to effect the power available at the tool... again, try visualizing filling your bathtub with a very long, skinny garden hose. The pressure (voltage) at the end will drop, and that could cause damage to your tools, or the electrical circuit. It's probably not going to be the case with the tools you are describing, but it's up to you if it is worth the risk of using the 50 footer when a 25 footer would do.

Start up is when current draw is usually highest. Make sure the vacuum is running before starting the saw, so you aren't hitting the circuit with both starting currents at the same time.

Doug
1 John 1:9
Fredericksburg, VA




http://disasterreliefeffort.org/
kp91 is online now  
post #5 of 23 (permalink) Old 06-14-2014, 09:12 AM
Registered User
 
BIG OLD TIM's Avatar
 
Join Date: May 2014
Country: United States
First Name: TIMOTHY
Posts: 48
 
Default

Zach...You are getting good information here. Having been a master electrician for past 36 years I would suggest you get an electrical contractor to give you a bid on adding some additional circuits, not just outlets. The lights dimming is a dead give away as to the existence of a real problem. Be sure to ask other residents in the home if other lights ever get brighter or dimmer when you start the saw. If so, I would really wait till you get the problems fixed before doing any large projects. As far as cords go...larger size and shorter is better!
Tim Drinkard
BIG OLD TIM is offline  
post #6 of 23 (permalink) Old 06-14-2014, 09:29 AM
RouterForums.com User
 
harrysin's Avatar
 
Join Date: Jan 2007
Country: Australia
First Name: Harry
Posts: 14,812
     
Send a message via Skype™ to harrysin
Default

I use master/slave switches on my saw and router tables which are programmable. when the saw is switched on there is a three second delay before the dust collector comes on, this ensures that the initial surges of the two tools don't co-inside and allows the saw to reach full speed before the Dust collector comes on. When the saw is switched off the dust collector runs for a further six seconds to collect residual dust. Because the router picks up speed almost instantly I only have a half second delay before the Dust collector comes on and it carries on for five seconds. The unit is in the far left corner of the saw bench.
Attached Thumbnails
Click image for larger version

Name:	master,slave-switch2a.jpg
Views:	73
Size:	87.9 KB
ID:	71551  


Harry



Nothing but heaven itself is better than a friend who is really a friend. - Plautus






harrysin is offline  
post #7 of 23 (permalink) Old 06-14-2014, 09:53 AM Thread Starter
Registered User
 
Join Date: Dec 2013
Country: United States
First Name: Zach
Posts: 40
 
Default

Thanks guys, super helpful.

I found an old kill-a-watt meter and tried it out on the setup, here are the results.

Miter saw only
Startup (Peak): 18A
Saw running: 7.5A
Saw cutting: 10A

Shop vac only
Startup (Peak): 12A
Running: 8.4A

Saw and Shop vac:
Shopvac running and then starting saw (peak): 21.6A
Both running: 16A
Both running and saw cutting: 18A

I notice the saw bogs down a bit while cutting and both are running, seems perhaps the motor isn't getting the juice it needs?

I think the answer is clear, I need to get one on another circuit. I thought these were interesting and wanted to share.

-Zach

Pax vobiscum
zm15 is offline  
post #8 of 23 (permalink) Old 06-14-2014, 11:14 AM
Registered User
 
RainMan 2.0's Avatar
 
Join Date: May 2014
Country: Canada
First Name: Rick
Posts: 16,816
 
Default

A 15 amp is typically wired with 14 gauge and I consider 14 gauge for lighting or walls that use very little draw like some of my living room circuits .
As mentioned your past the edge . I would have felt better if it was wired with 12 gauge which is a 20 amp circuit .

In the future I will need 90amps worth of circuits just to run my home theatre , and that's not including running the vacuum

Last edited by RainMan 2.0; 06-14-2014 at 11:45 AM.
RainMan 2.0 is online now  
post #9 of 23 (permalink) Old 06-14-2014, 11:24 AM
Registered User
 
RainMan 2.0's Avatar
 
Join Date: May 2014
Country: Canada
First Name: Rick
Posts: 16,816
 
Default

One other thing to keep in mind is a lack of current is very hard on equipment , motors and electronics etc . I'm sure Harry would agree
RainMan 2.0 is online now  
post #10 of 23 (permalink) Old 06-14-2014, 02:21 PM
jec
Registered User
 
jec's Avatar
 
Join Date: Sep 2006
Country: United States
First Name: Ed
Posts: 5
 
Send a message via AIM to jec
Default

An another good move would be to rewire the table saw to run 220v so it would not bog down at all and the motor would last a lot longer. Having an electrician come and locate the outlets so no extention cords are needed would be ideal!

jec is offline  
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Router Forums forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in











Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page
Display Modes
Linear Mode Linear Mode



Similar Threads
Thread Thread Starter Forum Replies Last Post
peak hp vs. real hp danapointed New Member Introductions 15 05-10-2017 03:33 PM
Craftsman v. Delta Tablesaws Thowie70 Tools and Woodworking 22 02-24-2014 10:12 PM
Router Backup yuva New Member Introductions 6 01-21-2014 08:33 PM
Peak HP dgcutter General Routing 22 01-10-2013 08:23 PM
All about Power Tools iconlife Tools and Woodworking 10 08-13-2012 12:09 PM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome